Quatro is raising the load to quickly

Is there a way to have a "soft start" on the generator load, my vitron Quatro is raising the load to quickly, would like to raise from 0 - full load over 2 min.

Generator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
JohnC avatar image
JohnC answered ·

Hi @Peter

There is, it's called Dynamic Current Limiter. Found in the Quattro's General settings.

But it doesn't take 2 minutes, more like 10 seconds or so. That's usually adequate for most gensets. If you're really after a warmup time or something, then this could be done with Assistants, but a lot more involved to set up.