Hi guys
Is there some way to show the kWh count for charging batteries from Grid or Generator? Can this be done via NodeRed/Signal K?
Thanks!
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi guys
Is there some way to show the kWh count for charging batteries from Grid or Generator? Can this be done via NodeRed/Signal K?
Thanks!
I'm using Modbus TCP with Home Assistant.
Take this for refference
https://www.victronenergy.com/upload/documents/CCGX-Modbus-TCP-register-list-2.90.xlsx
https://www.victronenergy.com/live/ccgx:modbustcp_faq
Here are the Unit IDs and Addresses for your counters:
Unit ID 227 Address 76 "Energy from AC-In 1 to battery"
Unit ID 227 Address 80 "Energy from AC-In 2 to battery"
Unit ID 227 Address 92 "Energy from AC-out to battery (typically from PV-inverter)"
#Home Assistant implementation
modbus:
- type: tcp
host: 10.0.0.50 # use the IP address of your CCGX
port: 502
name: victron
sensors:
- name: victron_energy_from_ac_in_1_to_battery_raw
unique_id: victron_energy_from_ac_in_1_to_battery_raw
unit_of_measurement: "kWh"
slave: 227
address: 76
data_type: uint32
scale: 0.01
precision: 2
scan_interval: 60
device_class: energy
- name: victron_energy_from_ac_in_2_to_battery_raw
unique_id: victron_energy_from_ac_in_2_to_battery_raw
unit_of_measurement: "kWh"
slave: 227
address: 80
data_type: uint32
scale: 0.01
precision: 2
scan_interval: 60
device_class: energy
- name: victron_energy_from_ac_out_to_battery_raw
unique_id: victron_energy_from_ac_out_to_battery_raw
unit_of_measurement: "kWh"
slave: 227
address: 92
data_type: uint32
scale: 0.01
precision: 2
scan_interval: 60
device_class: energy
template:
- sensor:
- name: "victron_energy_from_ac_in_1_to_battery"
unique_id: "victron_energy_from_ac_in_1_to_battery"
unit_of_measurement: 'kWh'
state_class: "total_increasing"
device_class: "energy"
state: "{% if is_number(states('sensor.victron_energy_from_ac_in_1_to_battery_raw')) %}{
{ (states('sensor.victron_energy_from_ac_in_1_to_battery_raw')) }}{% endif %}"
- name: "victron_energy_from_ac_in_2_to_battery"
unique_id: "victron_energy_from_ac_in_2_to_battery"
unit_of_measurement: 'kWh'
state_class: "total_increasing"
device_class: "energy"
state: "{% if is_number(states('sensor.victron_energy_from_ac_in_2_to_battery_raw')) %}{
{ (states('sensor.victron_energy_from_ac_in_2_to_battery_raw')) }}{% endif %}"
- name: "victron_energy_from_ac_out_to_battery"
unique_id: "victron_energy_from_ac_out_to_battery"
unit_of_measurement: 'kWh'
state_class: "total_increasing"
device_class: "energy"
state: "{% if is_number(states('sensor.victron_energy_from_ac_out_to_battery_raw')) %}{
{ (states('sensor.victron_energy_from_ac_out_to_battery_raw')) }}{% endif %}"
69 People are following this question.