Looking for Class K PV wire to comply with the MPPT RS manual requirement for individual strand diameters in the cable. I found some wire that meets the requirement, but the individual strands are tinned copper. Is that okay to use?
Specs of the wire I'm considering using to plug into the MPPT RS:
Single Conductor Wire
10 AWG Orange
10 Foot Package
Legend:
E196955 AWM 10 AWG OIL RESISTANT 600V VW-1 ARCTIC ULTRAFLEX BLUE® -55°C TO 105°C CSA 234608 TEW 105°C 600V FT1
Rated for and proven in extreme temperatures of -55°C to 105°C
This highly flexible wire combines finely stranded tinned copper with a jacket that resists the abuses of oil, gasoline, sunlight, saltwater, acids, and chemicals. ARCTIC ULTRAFLEX BLUE®has high abrasion resistance and can be used in most 600V applications. UL Listed as AWM (Appliance Wiring Material). Numerous applications including those approved under NEC article 400 and associated articles.
Features:
- Superior flexibility to -55°C (-67°F)
- Class K fine stranded tinned copper construction
- Resists oil, grease, chemicals, abrasion
- Sunlight and weather resistant
- Flame retardant (VW-1)
- UL Recognized and CSA Approved
- Environmentally safe
- Made in the USA
Applications:
- UL 508A Industrial control panels
- Internal appliance and equipment wiring
- Inverter cables and wiring
- Industrial machines and robotics
- Construction equipment
- Marine, RV and automotive wiring
- Medium and heavy-duty trucks and trailers
- Load banks, motor leads, welding cable
- Forklifts and golf carts
- Batteries and chargers
- Power hookup cable
Manufactured exclusively
by Polar Wire Products
-55°C to 105°C
Construction Specifications:
- 10 AWG
- Class K Tinned Copper Stranding (105/30)
- .120" Conductor Outside Diameter
- .030" Insulation Thickness
- .180" Finished Outside Diameter
- Ampacity at 30°C (86°F)*: 60
- Ampacity at 40°C (104°F)*: 56
*Ampacities of 600V and 1000V 105°C AWM wires in air. Ampacities based on single conductor in free air, 30°C or 40°C ambient temperature as specified, 105°C conductor temperature, per NEC table 310-17 (adjusted for 105°C). Free air ratings assume a one-cable-diameter space between adjacent conductors.