Victron Easysolar 2 GX system, 130a/h lead calcium batteries (24v). Short 50mm cables to batteries.
Are there any settings/adjustments to be able to bring the solar and system voltages closer to the real battery voltage?
I have a calibrated fluke multimeter on the battery which measures 26.01v - I have a chart recorder connected to the battery which also says 26.01v - I have a cheap ebay KG140 meter which reads 25.96v (50mV error) and then the Victron VRM remote console which measures 26.3v (299mV error).
I would have expected the Victron to be fairly accurate, but when the batteries are getting low at night, the battery voltage reads 24.1v and the victron system reads 24.4v. These measurements are when loads are quite light on the system.
Yes, I have connected the remote sensor terminals to the battery, but ithe Victron system always reads 300mV too high.
In a system where 300mV error is a big deal for a lead/calcium battery, I could do with being able to calibrate to account for the difference. Is this possible? Have I missed something?