Feature request multiplus Charge current control assistent

Hi


On the charge current control assistent, i would like to have the option to invert input.

As it is, i have make a connection on the temp. input to disable charging, but i would like to have an option to break a connection on temp. input to disable charging.

The reason I think this is a relavant option, is if there for some reason is a break in the signal cable it is better the charger stop charging on lifepo4 batteries for example.

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
boekel avatar image
boekel answered ·

You could use a pull-down resistor, but I think you should use the bms-assistant to stop charging, that one has the default setting so stop charging with an open connection.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Sten avatar image Sten commented ·

Thanks I would try that and se if it can do the trick. :-)