Generator on ACin1 of MultiPlus II 48/5000/70

We do not have AC Mains connected to this system and summer Airconditioning is using more power than anticipated. I have purchased this generator with a view to using it as "shore power" and have it charge the batteries and supply load when batteries are getting low.

Do I need to change any parameters in the Inverter/Charger?



Generator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
snoobler avatar image
snoobler answered ·

https://www.victronenergy.com/live/multiplus_faq


In addition to the above, if you have a grid code selected, it must be set to NONE, or it won't reliably charge from the generator without a large load.