So i have 2 5kw 24v multis set in parallel, when setting the current limit on the charger tab in Ve config, should i set to the total for both inverters, or half? ie.. if i set it to 20A, is that 40A in total or 10A per inverter
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
So i have 2 5kw 24v multis set in parallel, when setting the current limit on the charger tab in Ve config, should i set to the total for both inverters, or half? ie.. if i set it to 20A, is that 40A in total or 10A per inverter
Settings in ve.config are for each device in parallel, so setting 20a in each unit means 40a total for 2 units. You must load ve.config for each unit.