Pylontech stack limits

Hi Folks,

I currently have 12 x Pylontech US2000c battery's in one stack (in two columns of 6) with four power cables feeding top and bottom. This is running along side the Cerbo GX.

My question is I'm trying to determine if I should be running these with an LV Hub? And if not needed how many could I run without the hub?

Many Thanks

Pylontech
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

The "C" suffixed models can have 16 in a single stack without a LV hub.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

alexanderr avatar image alexanderr commented ·
Thank you, This was the reply I was looking for

Do you know where I can find the information on this?