How to stop Grid using electricity while I am 100% on PV and Battery

Good day all,


I noticed that the Grid is using 2kwh per day.

My system is completely running off PV during the day and battery during the night with 40% plus in the morning when the sun starts coming out.

My installer is talking about reactive power between Grid and Inverters....

2 x Multiplus II 48/5000

1 x RS 450/200

2 x Solar MD 14.3kwh batteries

28 x 400W IBC panels

Regards,

JHP

grid parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Jason - UK avatar image
Jason - UK answered ·

@Peyper Assuming you are set up using ESS mode, then yes, you will always take a little off the grid. If you want to reduce the amount you take from the grid, then set the grid setpoint to a negative value so you make sure you are always exporting a small amount and therefore never (or next to nothing) importing from the grid unless you have to.

1670257902880.png


1670257902880.png (65.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

peyper avatar image
peyper answered ·

@Jason - UK , Yes ESS setup. I had my very first Overload L1 warning this moring as the grid failed. We have scheduled grid shut down here in South Africa. My current load at the time of the grid failure was 500-700W, no more.

My grid setpoint settings was -30W, changed it to 20W

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

supec avatar image
supec answered ·

Anybody else tried negative Grid Setpoint to decrease using of the grid (my system is also sucking 1-2kWh per day with full battery - probably inductive cooker cycling?)?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.