Can the BMV 712 relay be programmed to operate on temperature?

The BVM 712 has a temperature option. And it can also monitor battery voltage. Can the relay in the BVM be programmed to force Victron Isolator to isolate battery on temperature and voltage?

BMV Battery Monitorisolators
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
boekel avatar image
boekel answered ·

Yes, you can use multiple relay options, see manual, DFLT is all 'or',


11. Relay mode DFLT Default mode. The relay thresholds Nos. 16 up to 31 can be used to control the relay. CHRG Charger mode. The relay will close when the state-of-charge falls below setting 16 (discharge floor) or when the battery voltage falls below setting 18 (low voltage relay). The relay will be open when the state-of-charge is higher than setting 17 (clear state-ofcharge relay) and the battery voltage is higher than setting 19 (clear low voltage relay). Application example: start and stop control of a generator, together with settings 14 and 15.


https://www.victronenergy.com/upload/documents/Manual-BMV-700-700H-702-712-EN-NL-FR-DE-ES-SE-PT-IT.pdf