Multiplus 2 wiring L1/L2

Hi everyone,

Is it possible to use phase L2 on AC-in and L1 on AC-out1? The reason is an ESS system with the loads on L1 (heating pump) and L2 is not used that much during nights when we whant the battery to be charged. Sweden grid with 3-phase.

Regards/Sebastian


Multiplus-IIESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Meine_Energiewende avatar image
Meine_Energiewende answered ·

No! That is not possible. One MP2 / Quattro can be used for one phase. Everything else would lead to a major short.

Jens