Tobias Franklin asked

ET112 ESS Distribution Board Installation

I am confused as to how to install my ET112 meter. I have a zigbee to send the meter info back to the Cerbo GX located in the garage.

(my setup is a DC coupled PV ESS install on a house in the UK)

Question 1: how do I wire in the meter? I need a simple-to-follow picture/diagram, my presumption is that is goes to the left of the main breaker switch and the live goes in position 1and out of position 2 with power from the Neural at the bottom?

Question 2: should I be running AC in to the inverter? At the moment I don't think I have setup the system to charge the batteries via any other means than via the MPPT. So should I run an AC in and also an AC out on the same cable that feeds the garage circuit?

Question3: I have 2 sockets running off AC out 2 - I wanted to have these as 'always on' even if there was a power cut but I can't see where you enable this output (the system isn't get wired into the house circuit which I was going to use AC out 1 for).


photo-2022-11-22-14-35-54.jpg

photo-2022-11-24-22-21-10.jpg

photo-2022-11-24-22-19-42.jpg

Multiplus-IIESSEnergy Meter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Jason - UK avatar image
Jason - UK answered ·

@Tobias Franklin

1. You need a means of isolation to the ET112 sub-meter so after the main isolator should be good. Also inside the consumer unit is best as installing the ET112 surface mounted is not advised as part of the L+N tails going into and out of the ET112 can leave a bit of the expose copper on show.

2. You mention you have a ESS system but the photos look like a stand alone / off grid set up with no obvious connection you your house AC distribution. Feel free to have a look at the photos on my VRM portal which show my set up and also my AC schematic.

https://vrm.victronenergy.com/installation/171934/share/db6807bb

3. AC out 2 disconnects in the event of a power cut to a ESS system. You would be better off taking the sockets from your main house distribution, and having the Multiplus connected to your house distribution that way both the house and your garage socketed use the power form your ESS system.