MPPT RS 450/200 Double String on one tracker both strings together have over 20A According to the data sheet of the MPPT, PV operational input current 18 A per tracker and Max. PV short circuit current 20 A per tracker My idea is to cover the north roof. The roof has 45° at Solar 180° North Central of Germany PVGis has 45-50% yield so I reduced the amps by 50% With ISC NMOT 8.4A so I think it should be allowed. Do you think you would do that too? Would you put diodes on both strings? Do you have source for suitable diodes?
MPPT RS 450/200 Doppel String auf einem Tracker beide Strings haben zusammen über 20A
Laut Datenblatt vom MPPT sind
Max. PV operational input current 18 A per tracker and Max. PV short circuit current 20 A per tracker
Meine Idee ist das Nord Dach zu belegen. Das Dach hat 45° bei Solar 180° Nord Mitte von Deutschland
PVGis hat 45-50% Ertrag somit hab ich die Amper um 50% gesenkt
Bei ISC NMOT 8,4A somit denke ich das es doch erlaubt sein dürfte.
Habt ihr bedenken würdet ihr das auch machen?
Würdet ihr Dioden setzen bei beiden Strings? Habt ihr quelle für geeignete Dioden?
https://mppt.victronenergy.com#djI7ZXlKdVlXMWxJam9pTXpJME5qa2dVR1YwWlhKemFHRm5aVzRzSUVSbGRYUnpZMmhzWVc1a0lpd2liR0YwSWpvMU1pNHpOelExT1RVeExDSnNibWNpT2pndU9UWTBPRGt6T0gwPTtjdXN0b20sNywyLDU0LC0xMCw3MCw0OCw5LDAuMDQsMTIuMzcsNDI1LDM2LC0wLjI1LDQzLjQsMTAsNjtjdXN0b20sNywxLDU0LC0xMCw3MCw0OCwxMS42MSwwLjA0LDEyLjM3LDQyNSwzNiwtMC4yNSw0My40LDEwLDY7Y3VzdG9tLDcsMSw1NCwtMTAsNzAsNDgsMTEuNjEsMC4wNCwxMi4zNyw0MjUsMzYsLTAuMjUsNDMuNCwxMCw2O2N1c3RvbSwzLDEsNTQsLTEwLDcwLDQ4LDExLjYxLDAuMDQsMTIuMzcsNDI1LDM2LC0wLjI1LDQzLjQsMTAsNg==