How does the Multiplus Inverter/Charger react during a low voltage alarm and high voltage alarm?

When the Multiplus is inverting, does a low cell voltage alarm (not pre-alarm) shut down the inverter, as in turn it off, or by some by other means? Similarly, for the Multiplus charger, is the charger isolated during a high cell voltage alarm? This is in the context of a system with Victron Smart batteries, Lynx Smart BMS, and Cerbo DVCC control.

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

From the manual:

  1. DVCC controls compatible devices via Lynx Smart BMS and a connected GX device. Charging current and voltages are set automatically, thus Bulk, Absorption and Float algorithms are no longer used. Charging or discharging are stopped at low or high cell voltage or low temperature.


Your MultiPlus is DVCC compatible (as long as it is connected via VE.Bus to your Cerbo GX).