question

ee21 avatar image
ee21 asked

Multiplus II split-phase w/TWO Current transformers?

Looking at implementing a split-phase 120v x 120v install with two units and ESS. Can a current transformer be connected to each Multiplus along with the two corrosponding main lugs, to monitor total current across both phase angles?


https://www.victronenergy.com/accessories/current-transformer-for-multiplus-ii

Multiplus-IIESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
shaneyake avatar image
shaneyake answered ·

Yes, each multiplus-II can have it's own CT but this will only work with MultiPlus-II 120V.

You will run them as L1 Inverter with L1 CT and L2 Inverter with L2 CT.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

servantlodestone avatar image
servantlodestone answered ·

We are considering a two-unit, ESS-powered, 120v x 120v split-phase installation. Is it possible to measure total current across both phase angles by connecting a current transformer to each Multiplus and its corresponding main lugs?

phrazle

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

shaneyake avatar image shaneyake commented ·
Yes. Both the power for each phase and the total.