please, can I use TOMZN TOB1Z-125 breaker in combination with Mega Fuses 125A between batteries (3x US3000C Pylontech) and Quattro 48/8000 + SmartSolar MPPT RS 450|100?


Cable is AWG 4. As it was packed with batteries.


thanks.

battery protect
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@zero

Having both is not necessary. If you add too much joins and resistance to a battery setup is has adverse effects.

Most daisy link the Pylons and fuse only the cables going to the bus bar. And each battery has an on/off switch.

You do need a few more US3000 batteries for an 8kVa Victron to meet min spec. Ideally 5 in total.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

zero avatar image zero commented ·
please, what is the reason for min spec. of 5 batteries? What can happened with only 3 units? thank you Alexandra