Can we connect two different battery (24V & 48V) system to one venus device?

I am having two independent battery systems.

1) This is my primary battery (48V) system with Victron smart shunt + Victron solar charge controller + Victron MultiPlus. All are connected to one venus device

2) This is my secondary battery (24V) system with Victron smart shunt + Victron solar charge controller + DC to DC charger. This is not connected to any venus device.

Can I connect both systems with one venus device?


Venus GX - VGX
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Biswa

The shunt for SOC monitoring, yes. But not the other 24v solar. The GX becomes an active controller (not that i have tried it) so may not work as expected?

You definitely would not be able to use anything smart like ESS and DVCC with both systems connected.

Though someone on this forum might have another way.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

biswa avatar image biswa commented ·

I was expecting that It may show two different battery systems instead one.untitled.png

0 Likes 0 ·
untitled.png (116.6 KiB)
Alexandra avatar image Alexandra ♦ biswa commented ·

That is not possible. The GX is dashboard is designed to monitor one inverter system.

You can have it show at the bottom like the multiplus is showing.