Multiplus 1 & G99 compliant relay DNO acceptance

Has any one had experience of getting a Multiplus (1) 5000 and a UVFR G99 relay through DNO compliance for a grid connection in the UK ?

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

I would not expect this to be accepted even with a UVFR.
The older MultiPlus 1 devices, due to hardware limitations, are not G98 or G99 compliant for grid interactive operation, I think you already know this. A good DNO would simply reject it based on that fact that it has no certificate.
A UVFR device would not suffice because it's only half of the picture, it would only respond to Voltage and frequency conditions. A grid interactive compliant device also needs to respond to certain reactive conditions while it remains connected.