Has any one had experience of getting a Multiplus (1) 5000 and a UVFR G99 relay through DNO compliance for a grid connection in the UK ?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Has any one had experience of getting a Multiplus (1) 5000 and a UVFR G99 relay through DNO compliance for a grid connection in the UK ?
I would not expect this to be accepted even with a UVFR.
The older MultiPlus 1 devices, due to hardware limitations, are not G98 or G99 compliant for grid interactive operation, I think you already know this. A good DNO would simply reject it based on that fact that it has no certificate.
A UVFR device would not suffice because it's only half of the picture, it would only respond to Voltage and frequency conditions. A grid interactive compliant device also needs to respond to certain reactive conditions while it remains connected.