Multiplus II 48/3000 with 42V battery (7x6V) possible

Hello, I was trying to find a thread with this question but didn't find it. So hopefully it is fine to open a new thread. My situation is that I have a 48V battery bank with 8x6V lead batteries. One of these is damaged and the others seem to be in very good state, still. I am planning to run now 7x6V in series with a Multiplus 2 48/3000. The nominal input voltage is defined as 38-66V according to the data sheet. My question is if I can change the voltage-settings for the battery charger like absorption-voltage or float voltage to adjust it to the 42V battery bank? And are there other issues why I should not do this (except a smaller power)? Thanks a lot!

chargerbattery system voltage
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
kevgermany avatar image
kevgermany answered ·

I ran this through Victron connect in demo mode. Seems the lowest float voltage you can set is 48V, and lowest absorption 50V. Up to you, but I think not.

If one battery, you'll probably be ok replacing that one. Not recommended practice, but probably get you the remaining extra life of the others

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

dannyd avatar image
dannyd answered ·

Hello kevgermany, many thanks for your prompt response and the good idea to run Victron Connect in Demo mode. I retried and I could set the absorption to 48.1 (instead 50V), but this is not a game changer in this issue. So I will get a spare battery (possibly even a second hand one). Regards

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic

Chargers.

Additional resources still need to be added for this topic