Fronius Symo AC-out, VRM/GX Dashboard Critical Loads measurement

Hi,

we installed a Grind connected System with an Innovenergy Salidomo battery and a Fronius Symo on the AC out in ESS Mode (1:1 rule regarded). Everything works fine. But on the GX/Dashboard overview I see on the circuit diagram as the inverter is connected to the AC in and not AC out. Not too bad, but visualized critical load is the sum of critical loads and PV power, so therefore it is confusing that during the day the critical loads go to zero when production is higher than consumption. Is ist possible to change that so that critical loads is shown correctly?

In my oppinion the position of Inverter should be set on AC_in or AC_out, therefore a internal calculation can estimate the true value for Critical load.

Multiplus-IIESSVenus GX - VGX
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Meine_Energiewende avatar image
Meine_Energiewende answered ·

You have to "tell" the system where your fronius symo is connected to:

-> Settings -> PVInverters -> Inverters -> "Inverter Name" -> Position.

You have to choose AC-Out there.

Hope it helps

Jens