no load power consumption

Because high power inverters use more idle power than low power inverters, is it possible to parallel 2 or more victron multiplus inverters on low power 3000va and only have one inverter active, with the others in standby (not drawing no load power) until the 3000va power is exceeded? is this possible?

powerassist
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Kevin Windrem avatar image
Kevin Windrem answered ·

No. Parallel Multis will always be in the same mode. The only way to shut one of a paralleled Multi down is to physically disconnect it's AC ins and outs and the DC connection then reprogram the other unit to function as a standalone.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

@Kevin Windrem

The only way to shut one of a paralleled Multi down is to physically disconnect it's AC ins and outs and the DC connection

Can you explain why all this disconnecting is needed?

I just turned the unused units of and reprogrammed active ones for single configuration.

0 Likes 0 ·