ESS : how don't use battery to power the charges on AC-IN?

Hi


I have multiplus 2 with battery and et112 on the grid. Currently th battery are used to power the charge on the AC-IN and AC-OUT .is it possible to use the battery power only for the AC-OUT ?


Thanks


Regards


Damien

ess discharging
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
sharpener avatar image
sharpener answered ·

Not directly, because the AC-In and AC-Out are connected together by the anti-islanding relays when the grid is detected.

But if I understand your question correctly...

...if you make the Grid Setpoint = 0 and also put the loads that are connected to AC-In on the grid side of the ET112 (or use the internal current transformer instead) they will be "invisible" to the Multi and then it will control the inverter power so as to provide only enough for the loads on the AC-Out.