BYD LVS 4 setup

Hi Victron community.

I'm setting up 6 x BYD LVS 4's onto a DC bus for a 3 phase Multi II off-grid system.

The Be Connect config app asks for Single OR Three phase configuration.

Am I right in thinking it should be Single phase onto the DC bus?

Thanks in advance, Marc

BYD
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Stad

You have a three phase inverter system, so set the BMU for 3 phase.