victron Error #67 on MPPT (BMS connection lost) on smarsolar 150/45

I get this error "Error #67 on MPPT (BMS connection lost)" on smarsolar 150/45 today after restarting the raspberry pi that functions as the GX.

I have no BMS connected but did install the driver to do so vir rs486


Raspberry Pi
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
elvis avatar image
elvis answered ·

If you don't have a BMS connected the victron recommended solution is to factory reset the mppt

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

perry-westphal avatar image
perry-westphal answered ·

I solved this issue last month.

To simulate the problem:

Disconnect all mppt´s and repower CERBO.

When connecting a mppt, the cerbo immediately goes into error 67 (BMS connection lost)

Solucion: Replace CERBO