question

marnix avatar image
marnix asked

How to connect Phoenix Smart Inverter 24/2000 with VE.Bus BMS

I have a Phoenix Smart Inverter 24/2000 and a VE.Bus BMS.
The inverter doesn't have a VE.Bus connector.
How do I connect these two?


Below the picture with the available connectors.
Do I need an additional cable?

schermafbeelding-2022-10-13-om-120920.jpg

Phoenix Inverter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

@Marnix

The VE.Bus BMS has a Load disconnect output. You need to wire this to the Remote H pin on that green connector of the Inverter (don't forget to remove the wire loop).

See also: Remote Connector in the Phoenix manual