How to reset Multi RS SOC?

Is there a way of resetting the SOC readout on the Multi RS Solar? As can be seen, Voltage is at 58V and charging current now down to 2.4A. Batteries are brand new 200Ah LiFeP04.

The inverter went into low battery volts on the start of a 1.5kW pump with no AC IN connected. SOC meter went from 86% to 1%.

1665628647495.jpeg

Multi RS
1665628647495.jpeg (91.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi @lintech,

To reset the state of charge (SOC) on the Multi RS, you will need to enable "Expert mode" in the battery settings in VictronConnect;

cleanshot-2022-10-13-at-151000.jpg

Then scroll to the bottom of the battery settings and you should see a button to Sync to 100%.

cleanshot-2022-10-13-at-151412.jpg


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

lintech avatar image
lintech answered ·

Currently I am having to reset this SOC display every couple of days as it works it's way down to about 36% when fully charged. Is there a specific method for calibrating this SOC reading so it doesn't need to be reset all the time?