I have two Multiplus ii 230v in parallel operation and one Cerbo GX. Does the Cerbo GX recognize 1. each Multiplus as one combined single unit, 2. each Multiplus as individual units, or 3. does not work in this configuration.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I have two Multiplus ii 230v in parallel operation and one Cerbo GX. Does the Cerbo GX recognize 1. each Multiplus as one combined single unit, 2. each Multiplus as individual units, or 3. does not work in this configuration.
The two units must be configured for parallel operation, then they appear as a single unit on Cerbo.
tThis would be the same for three units in a 3-phase system.