question

pfloryann avatar image
pfloryann asked

Failed ESS grid set point following

Hi,

I using 2 multiplus ii 5000/48 in parallel and i disabled the grid feed-in from Ess and i set the grid setpoint 0 ..But he continues to have grid feed-in 30-200w...IS NOT ARROUND SET POINT.

With an single multiplus with the grid setpoint 0, feed-in it was accepatable 0.1-0.2kw per day , but with both multiplus in parallel is more than 1kw per day !!! i don't want this.

I found a temporary solution with setpoint at 100w+. But I don't want to take it 100w from grid when it's sunny outside or when I'm using the batteries.

My System: 2 x Multiplus II 5000/48 (paralell), 1 x Smartsolar Mppt 150/100, 1 x Smartsolar Mppt 150/70 Tr, Bmv-712, Venus Os 2.90, 3x battery balancer, battery bank 500Ah at 48v, 7.2kw solar panels.

Please help me to solve this problem. Thank you!

screenshot-20220926-160422-comhuaweibrowser-edit-4.jpg

screenshot-20220926-160422-comhuaweibrowser-edit-4.jpg


gridfeed-in limit
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
rata1 avatar image
rata1 answered ·

Hello,

I was struggling with this. See my post here - https://community.victronenergy.com/questions/176430/what-is-the-correct-current-sense-configuration-fo.html?childToView=179159#answer-179159

Nobody replied or commented so maybe it is just you and I that have this unacceptable issue ;)

It might work for you.

Let me know if it does.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.