I want to prepare all installation and wiring for a system with the EasySolar-II-24V-3kVA-MPPT-250-70.
As I don't have the PV panels and batteries yet, can I safely switch on the system and use on the grid only (with load on the outputs?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I want to prepare all installation and wiring for a system with the EasySolar-II-24V-3kVA-MPPT-250-70.
As I don't have the PV panels and batteries yet, can I safely switch on the system and use on the grid only (with load on the outputs?
No. As most of the settings require battery reference . One example of its operation is power assist.
You will see DC ripple warnings and potentially damage the power pack.
Wire a bypass switch in so you can prepare your install Wiring etc and when your batteries are delivered, connect, program and go live.