Easyplus 12/1600/70 with generator use ac out 0 (bypass) off when vacuum cleaner (2400w) switched on

I have newly installed easyplus and connected a generator 5kva honda+sincro into ac in. 460 Ah flooded batteries. When charge mode on and using ac out0 to use heavy duty equipment like vacuum cleaner 2400w the dc charge and ac out cuts off immediately when switching vacuum cleaner on. 700w coffee maker works fine. What could be the problem. It should bypass 16A? After some tens of seconds the charge and ac out0 is back.

GeneratorEasyPlus
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
klim8skeptic avatar image
klim8skeptic answered ·

It sounds like the sudden load of the vacuum is altering the generators voltage/frequency to the point. that the multi opens its feed relay (and the relay K, output 0).

Have a read of the MultiPlus generator FAQ's.