Hello!
When I have 3x Multiplus 2 3000 and a Fronius Symo 5kW on AC-out and the grid is down, then the power from the Symo is usable for my essential loads > ok.
My question now:
When the Symo produces for exmaple 5kW, i guess that this power comes evenly on all 3-Phases, right?
So whats happening when battery is full and i need 3000W only on Phase 1 !?
The Multiplus only can do about 2400W, if the rest (600W) comes from the Symo then i have also 600 Watts on Phase 2 & 3 without a consumer...!?
...so i think with full battery and without a "base load" on all 3-Phases, only the 2400W from the Multiplus are usable, right?