Multiplus 24V 3000W doesn't discharge batteries under 85%

Hello,

I have two systems based by Multiplus 24V 3000W, one with MPPT 150/70 - 2 x 12V/250A Ultracell, 6 x 395W Trina PV, other one with MPPT 150/85-Tr - 2 x 12V/220A Victron AGM, 6 x 405W Trina PV. These are separate systems, no parallel connection, feeding different consumers.

On the 150/70 version I discover that the system put the batteries in idle at 85% and feed the system from the grid, the 150/85 goes to 50% discharge. I compared the two VE Configure files and the setting seems to be almost identically (the difference is the batteries capacity). What I' am doing wrong with the 150/70? Many thanks for your help.

multiplus ve.bus
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Mike Dorsett avatar image
Mike Dorsett answered ·

Try setting "ignore AC in" on the 150/70 system.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

manone avatar image manone commented ·
Thanks for your reply, I will try tomorrow morning, I can't connect Venus GX (Remote Console) anymore.
0 Likes 0 ·
manone avatar image
manone answered ·

L.E. I did a firmware update to Multiplus but now it's showing batteries at 100% with 23.7V which is far below to readings of the other system which have 52% at 24.55V. It seems that doesn't read the values correctly, can you help with this issue? Also I get a "low battery" warning from Multiplus...

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.