Multiplus Pass Through

I currently have two Multiplus 3000 12v, one on each leg supplying power to my RV. We have been running for slightly over one year with no issues while running both generator and shore power.

Now AC-1 IN is working on shore/generator power no issues. This Multiplus is the charger.

AC-2 IN is showing voltage and HZ but will not pass through. This multiplus is only inverting.

Does the multiplus 3000 have any internal fuses or contacts which could be the problem?

a9ef6a4f-ea36-4a54-9169-1223179f6c05.png

4501e5ba-9081-4f4b-a27f-c69153cd10be.png

multiple inverters
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
jadkins avatar image
jadkins answered ·

Just FYI I found the problem!!!! This was a SHORE POWER problem. Assuming at this point the resort has the ground and neutral inverted on one leg.