Multiplus Compact 12/1600/70-16 goes in Alarm when connected to shore

Hello! :)

Hopefully you guys can help me up with the trouble shooting / config of my system.

It goes like this:

Shore -> multiplus -> 12V LIONTRON Lifepo

Also I am using a Smart shunt and a cerbo GX via VE.Bus. Firmware is 430.


The system is working fine, until I plug in the shore cable. Then the system shows the red alarm light an the following messages on the cerbo display.

Alarm - temperature high

Alarm - error temperature sensor

Alarm - battery low

The voltage is 13.11V, temp 29 C

When connecting the shore line, the voltage drops to 8.07V DC.

AC-line shows 95V due to the connected generator. Also it shows -1.3A, which I don’t understand.


Could you guys please put me on the right direction to solve the issue?

Thanks!

Temperature Sensoralarmshorepower
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mike Dorsett avatar image Mike Dorsett commented ·
Are you using galvanic isolation (transformer) for your shore connection?



0 Likes 0 ·
2 Answers
dna avatar image
dna answered ·

CCE - Breaker circuit - easyplus (multiplus with breakers)

No additional isolation other than the built in in the easyplus

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

dna avatar image
dna answered ·

c16ca274-f13e-4412-ab5c-9b4c9766d037.jpeg

Some photos of the screen


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic

Victron temperature sensor disambiguation table - which product supports which sensor