High load assistand.

Is there a way to make a ESS system switch to mains supply if there is a preset load for a preset time. ?

ESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Murray van Graan avatar image
Murray van Graan answered ·

Unless in case of a grid failure, an ESS system is always synchronized and connected to the grid. You could disable discharge for a preset time by enabling a scheduled charge, setting it up around your load