dsedgman asked

Large scale system design

Hi there everyone.

I have been involved in the renewable energy sector for a number of years now, and have installed many small scale systems but have been asked to be involved in the design and install of a large scale system. I understand that 6 x 15kw multiplus II units can be connected in parallel totalling 90kw for one phase, and that three sets of these can be connected together for a three phase installation. So that would be a system totalling 270kw for the 3 phase installation.

This would be sufficient for the first stage of the project, but as the project is expanded in years to come, is it possible to add another independent 270kw system to the existing installation on a common three phase bus supplying the facility?


Thanks in advance,

Daniel.

system designmultiple inverters
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

The maximum for one system is 180kVA with 12 of the 15kVA Quattro (4 on each phase).

https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems

Connecting multiple systems together is not possible or at least not recommend/officially supported.