MultiPlus PC backup Inverter size and load

I want to make a backup system for my PC+Server but i really don't know what size inverter i should chose.

My normal load is 450W-550W but when everything is on max usage it's around 900-1000W. So i'm wondering if a 800VA multiplus would handle being overloaded to around 1000W for about 10 seconds

MultiPlus Quattro Inverter Chargerups
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nickdb avatar image
nickdb answered ·

Inverters will derate due to temperature at higher load, so I would suggest you size the inverter correctly for the larger output, especially since it is sensitive gear. Unless you don't mind the inverter turning itself off.



1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

xpatrik avatar image xpatrik commented ·
The inverter would be idle most of the time. High load only when the grid fails