We are currently using a cerbo gx with nothing connected to the CAN Interfaces. Is it necessary to terminate these please.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Each CANbus on Cerbo has TWO RJ-45 connectors so a termination IS required for each bus if this is "the end of the line". There's no reason the bus can't run through Cerbo to other pieces of equipment.
And no you do not need terminations plugged in if you aren't using the bus.