Hi.
As the title says, my multiplus still pulls about 25 watts from the grid when
1)the power button is on the "off" position
2)the batteries are disconnected
3)the cerbo is off
(conditions 2) and 3) are there just to be sure that what I'm seeing is related only to the multiplus and there is no strange interaction with other components in the system).
I've measured these 25 watts with a current clamp on both line and neutral connected toAC-IN of the multiplus.
Also, the multiplus actually stays warn (so there is some load in there that is still powered and it's not a fault of the current clamp).
Does anyone know if this is normal behaviour or not? And, in both cases, does anyone have any idea of what and why is causing this?
Thanks