xtopher asked

Victron MODBUS with Home Assistant - strange register behaviour

Hi all,

Has anyone seen an issue with register 789 - 'PV power' on the MODBUS? I've seen that it reports properly a lot of the time but I've just seen it go a bit haywire and report negative completely unrealistic numbers, then after an amount of time goes back to normal? It made my HA dashboard go nuts as it couldn't balance the readings so was reading zero for PV Power when it was actually it was at multiple KW output


Here is an example in HA - number has gone negative:1661339818812.png


And history graph, see it is often giving negative reading?

1661339900918.png


Actually managed to get them together using remote console:


1661340171650.png


Any ideas why its going negative?


Here's the config:

1661340448166.png


1661340490938.png



This is with a MTTP RS 450/100, Multiplus II and Cerbo GX (f/w: 2.89)

Modbus TCP
1661340448166.png (82.4 KiB)
1661340490938.png (25.2 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

xtopher avatar image xtopher commented ·

Digging a bit more it appears it can't ever report over 3.2kW? If it goes over that then I get the crazy negative numbers? I'd not been using this register until recently as I'd just been using the 'yeild today' in HA to get it to display on the historical energy graph. Now I'm trying to output near real time numbers I've started to use this 789 register.


This is the past week:

1661340934619.png


Its almost as if it goes over 3.2kW, its then reporting negative the same value rather than the ~5+kW that is actually being generated?

0 Likes 0 ·
1661340934619.png (100.1 KiB)
1 Answer
xtopher avatar image
xtopher answered ·

OK think I've been using the wrong register, I should be using the highlighted one below, that is giving the right reading

1661341819910.png

Any ideas why the details for Tracker 0 and Tracker 1 appear to be the same? Should they have different addresses? Seems like a typo? I don't need the individual tracker details but could be handy.


1661341819910.png (47.5 KiB)
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

xtopher avatar image xtopher commented ·

@Guy Stewart (Victron Community Manager)@mvader (Victron Energy) - looks like there is a typo in the CCGX Modbus register list spreadsheet (2.80)


As above comment, 'PV power for tracker 0' should be Address 3724 (not 3725). **Note I've added column A above to track by unit ID - that is not in the spreadsheet.

0 Likes 0 ·
mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ xtopher commented ·
Hi @Xtopher thank you; noted. We'll fix that. Matthijs
1 Like 1 ·