Parrallel Multiplus II 48/5000 - maximum transfer load

As we can't use the Multiplus II 48/10000 due to no G99 certification we may need to use two Multiplus II 48/5000 in parallel.

The transfer switch is rated at 50A, does that mean that two in parallel can transfer 100A?

I know all cables AC & DC need to be the same length.

PS. I have a separate question relating to using the Quattro 48/10000 instead.

multiplus in parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
daniel-feist avatar image
daniel-feist answered ·

2 x 50A would be 100A in parallel, yes. What I'm not clear on though, and I asked in a separate thread, is how to interpret the 50A maximum. i.e. is it continuous/peak etc?