mark-hawkins avatar image
mark-hawkins asked

3600 transformer connector question - J34 to J34A

Hello. Please could anyone help with my 3600 transformer connector question - wire from J34 to J34A.

5 years ago I purchased a steel narrowboat and asked a electrician to fit a Victron Transformer 3600 when floating in water. After 5 years with the steel boat in water, the Victron 3600 case was removed and saw that the wire (green yellow) was connected from J34 to J34A.

When the boat is in water should this be?

Connect PE to J34A
Remove J34 to J34A

I have attached a link to the manual - Page 7

https://www.victronenergy.com/upload/documents/Manual-UK-IsolationTransformer1800-3600.pdf

I am hoping the electrician has not made a mistake.
Could be my boat has not been protected for many years. Does it still protect the boat with the J34 to J34A connected when in water and is it just a safety feature when on land?

I appreciate any help on this.


Isolation Tranformer
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
pwfarnell avatar image
pwfarnell answered ·

With a steel narrowboat the isolation transformer is being installed to separate the boats hull from the shore power earth to avoid galvanic corrosion from stray earth currents. To keep them separate when in the water J34 should not be connected to J34A nor should the PE wire be connected to J34.I

If you have had a connection to J34 then you would not have protection from galvanic corrosion but the system would still be safe, i.e. your RCD breakers on the boat would still work and protect you if there was an electrical fault to ground. It would be as if you had a direct shore power connection without a galvanic isolator. This only matters when you are on shore power, have you been hooked up for the 5 years.

The connection to J34 is made when on land is I believe for electrical safety. my understanding is that when you are in water if there is an earth fault, the boat hull can discharge the voltage into the water so you could not get a shock if you touch the boat with one hand and the dock with the other. However, if you are on land and there is an earth fault the hull could be at a high voltage because it can not dissipate that voltage to ground, therefore someone could get a shock from your hull.

On my narrowboat I had built last year I specified an IT and one of the first checks I made was to use my multimeter to see if there was a connection between the shorepower socket earth connection and the boat hull to confirm that they were not connected.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mark-hawkins avatar image
mark-hawkins answered ·

Thank you pwfarnell. I really appreciate your help. I have been connected to shore power only for 5 years. Never unplugged. I'm taking my boat our for blacking this month so I will see if I have any galvanic issues. I feel very gutted the transformer instillation was not done correctly in the first place and left without protection. Hopefully my anodes have done their job.

2 |3000