I switched on the 10kVA quattro with 6x US3000C pylontech batteries at about 50% charge.
I later programmed the charger tab, 52V bulk, 51V float, 46V cutoff (AS NORMAL, according to the other 30 odd installs I've done with Pylon)
Soon as I sent the settings and they installed, inverter won't switch on. "LOW BATT"
Voltage was 49.5V
I had to change batteries to switch on again and set low cutoff to 44V, problem "solved".
But not solved. Because Pylon needs load switched off at 46V absolute minimum.
Inverter firmware at 481.
Had the same problem with same Pylon batteries on Multiplus II 5kVA, but the low battery error was constantly showing on its previous set of Trojan sealed floodeds (I believe this inverter to be faulty...) and it would not switch on in first place, before even setting cutoff of 46V. Trojans would have been 37 to 43, somewhere there..