installed 4 pylontech batteries through Multiplus II GX inverter andMPPT 250 controller . no mains . After 3 weeks its now giving low battery on the inverter and all batteries are in alarm . Battery vlotage is 56.7 V .

What do i need to alter in the settings


low battery warning
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
jeanmarie avatar image
jeanmarie answered ·

Hi,

which pylontech model are you talking about?

Because standard ones are 15S models, meaning 56,7V for the pack correspond to 3,78 per element : this is bad for your battery life

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image
nickdb answered ·

Go step through the pylon setup guide properly. It sounds like something is misconfigured.

https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom

At that voltage, if it is correct, you will be trying to cook the battery.