PowerControl et PowerAssist

Bonjour,

Mon TGBT sera raccordé à la sortie "AC out" du Multiplus-II/8000VA.

Sur le disjconteur ERDF, il n'y aura donc rien d'autre que "AC in".

Dans ce cas de figure, est-ce que les fonctions "PowerControl" et "PowerAssist"
seront fonctionnelles sans ajouter la sonde de courant 100A ?

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
johanndo avatar image
johanndo answered ·

Power control (AC input current monitoring) and Power Assist (Output power supply by the inverter) work without an external current sensor. The Multiplus internally measures the power and reacts if this functions are enabled.