How many MP2's can be controlled/monitored by a single CCGX via VEbus?

Putting a three phase system together with multiple MP2's. I want to know how extendable the VEbus system is?

CCGX Color Control
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
boekel avatar image
boekel answered ·

https://www.victronenergy.com/upload/documents/Datasheet-MultiPlus-II-inverter-charger-EN.pdf

6 per phase, so 18 units in a three phase system.
But you might want to look at the bigger Quattro units for a large system.