question

Michael Timler avatar image
Michael Timler asked

Multiplus II: 3-Phase-System: Can I switch off L2 and L3 inverter and run L1 solo?

Have installed and configured three Victron Multiplus II - 5000/48 as a 3ph System in an Off-Grid constellation. For power saving reasons I would now like to switch off the inverters for L2 and L3 during night times and connect all loads, that need to be alive, on L1.

Is there any strategy to configure the system to achieve this?

Thank you for input!

Michael.

Multiplus-II3 phase
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

6 Answers
Mike Dorsett avatar image
Mike Dorsett answered ·

No, the system needs to see all 3 inverters "ON" in order not to go into error mode. The only way to get some power saving is to enable AES. This can save up to 50% energy during low power periods. It helps also to keep the loads evenly balanced so the load on each inverter is less than the AES threshold.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image
marekp answered ·

@Michael Timler

You can add fourth smaller just inverter and use it for the night loads when main system is switched off.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Michael Timler avatar image Michael Timler commented ·
Good idea in general. In my particular project I need the night energy for running a freezer with high starting currents. Very low overall consumption otherwise. Well, I am afraid to have to leave it as it is....

Thank you very much for your input!

Michael


0 Likes 0 ·
Michael Timler avatar image
Michael Timler answered ·

@Mike Dorsett

Thank you very much for your clear answer.

Anyway, are you sure, that AES works in 3ph-systems?
Due to the handbook, it's said, that this only works in single mode.

Could you confirm this?


Thank you very much!

Michael



1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Meine_Energiewende avatar image Meine_Energiewende commented ·

AES will not work on a 3 phase system.

Jens

1 Like 1 ·
marekp avatar image
marekp answered ·
@Michael Timler

For that freezer you can install "slow start" unit to take care of the inrush current.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Michael Timler avatar image
Michael Timler answered ·

No, unfortunately, from all what I know, you can't.

Every heat pump or compressor (and a freezer is nothing else) has to overcome the pressure against the dead center point on start.

A slow start unit does nothing else than limit the power to the load on start. However, limiting the power in the moment of utmost power energy demand of the motor against the gas pressure on dead center point means, that either the motor will get stuck and burn down, or, in case the slow start unit is a good one, the motor will NOT start to rotate at all, or, if the freezer motor has protection, its current limiter will respond. Some heat pumps have a mechanical decoupling in the moment of start, combined with a mechanical flywheel mass, however, freezers have to stay affordable units and therefore the expenses for such gimmicks are too high.

Test it yourself! Stop your freezer when running by interrupting the power supply and then plug it in some seconds later. You will have a good chance, that the thing refuses to start for some minutes, until the coolant has released its pressure via the expansion valve. This is usually the case during normal operation, but not, when the plug is briefly pulled. It may well be, that the motor protection will respond for quite a while, until even the background power of a public grid is strong enough to overcome the rest pressure inside the coolant system for just this one particular millisecond.

In case of electric motors built in bigger electric angle grinders, for example, that do not have to overcome any dead points on start, a slow start unit works perfect. And in case of most inverters, they have that inbuilt anyway.

Thank you for your input and if I missed something in my statement or put something wrong, please let me know.

Michael

14 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·
@Michael Timler

There are 2 types of a slow-start units.

1. based on power limiting that use thyristors. Motor gets less power at the beginning and full power at the end. This method is the one you are describing.

2. based on frequency adjustment. Motor gets full power from the beginning but at lower frequency, therefore motor is rotating slower. When frequency is slowly raised up to the nominal value motor is slowly increasing its RMPs up to nominal.

I have a Heat Pump at home that uses that second method at startup.

I am not saying that that second method will work for your freezer. You should ask someone who knows your freezer for opinion on this mater. There may be a problem if the motor is a single phase type.

0 Likes 0 ·
Michael Timler avatar image Michael Timler marekp commented ·

Thank you for your correction! Very much appreciated.

But the point is: In a compressor-like heat pump you have to have the torque to overcome the counter force at the moment of start. In addition, you have the mass inertia of the accelerating motor.

No matter in which way you try to "fade in" your energy fade up, either frequency or pulse width manipulation, both has the same result: In the moment of utmost power demand the mechanic doesn't get the energy to overcome the dead center point.

Because that's the way my freezer is constructed. After that first moment, the rotation motor has built up enough flywheel mass to overcome the next dead center point, that the freezer runs using 70W only.

But in the moment of start, it needs way more than 2000W (an inverter of that size, having inbuilt startup capabilities, can't move the thing, I have tested that before.)

Let's take an example: If you pull a nail into wood, you can either press the nail in using a leverage press (which would be according to a soft start unit) or you can use a hammer (which compares to a electrical grid with endless power reserve). Let's assume that we need a force of 1000kg (which is physically not correct, but just for easier imagination) to drive the nail in.

What will happen with the nail, if your leverage press only has 800kg max. available? It can't provide more, because the lever of that press would brake otherwise (According to our electrical motor, that would burn down, when receiving that much energy without being able to turn). Would it help to soft-start the leverage press up to that maximum point? No, for one millisecond, your load (the nail) will need a force greater than 1000kg and if you can't get this from your energy background, the nail will not move.

What do you think?

Michael



0 Likes 0 ·
marekp avatar image marekp Michael Timler commented ·

@Michael Timler

I agree with you, and this is why I suggested to consult this with local supplier of such slow-start unit.

It could be possible to use a slow-start after selecting the startup speed correct for your freezer. Even half a second startup time could lower the inrush current significantly.

It depends on the type of the compressor.

In my heat pump I have scroll type and it works but slow-start was selected and programmed by the maker of the pump. But it is a 3 phase unit so it is much easier to do.

I never used it but Victron Phoenics 1600VA inverter should be able to work with your freezer without slow start if the inrush power is less than 3kW.

https://www.victronenergy.com/upload/documents/Datasheet-Phoenix-Inverter-Smart-1600VA-5000VA-EN.pdf

If not that one there is a stronger one 3000VA with 6000VA peak power.

https://www.victronenergy.com/upload/documents/Datasheet-Phoenix-Inverter-1200VA-5000VA-EN.pdf

Extra start-up power

A unique feature of the SinusMax technology is very high start-up power. Conventional high frequency technology does not offer such extreme performance. Phoenix Inverters, however, are well suited to power up difficult loads such as refrigeration compressors, electric motors and similar appliances.

0 Likes 0 ·
Michael Timler avatar image Michael Timler marekp commented ·

Hm, I have provided, that the inrush current is not the problem.

I have provided, that this is a mechanical problem of the construction of this particular type of heat-pump. And I have provided, that I have used a 1200VA inverter (Victron Phoenix 48-1200 with 2200Wp), that couldn't start the freezer, and I have provided, that even the grid doesn't start that particular freezer after plugging out and in during run, because the motor isn't strong enough to overcome counter-pressure as long as the expansion valve hasn't degraded the pressure inside the compressor. I can't find any argument, that could bring that further.

Your heat pump must have accompanying mechanical constructions that minimize the coolant pressure. It has probably not a fixed expansion valve and it has a much stronger electric drive to manage the much stronger overall energy turnover. Such drives must have a soft start or kind of frequency modulation, otherwise your lights in the house would flicker, when the thing turns on.

I assume, that your heat pump first of all opens the expansion valve, as soon as the motor stops. This has the effect, that there is no counter force or upper dead point at all anymore. The coolant pressure in that moment is the same all over the gas system. In scroll type pumps, the upper center point effect is mechanically minimized anyway. Just because to get soft start capabilities from the mechanical side.

My freezer obviously is an old fashioned construction with a fixed and therefore uncontrolled expansion valve as almost any cheap freezers are constructed. However -besides the start problem- my old guy almost doesn't need any energy and runs on very low overall consumption rates.

No matter how: Thank you very much for your input and time, because it forced me to think myself deeper into that manner and any input and experience is helpful to do so.

Michael

0 Likes 0 ·
marekp avatar image marekp Michael Timler commented ·
@Michael Timler

Thank you for the technical explanation of how the compressor works. Really, I did not know such details.

As for my Heat Pump, they sell them with and without slow-start unit. It depends on the size of the compressor. Mine has a fixed expansion valve.

I suspect your freezer has piston type compressor that has low startup momentum and single phase motor.

Mine is rotary and 3 phase.

How your freezer deals with short power outages?

0 Likes 0 ·
Michael Timler avatar image Michael Timler marekp commented ·

"I suspect your freezer has piston type compressor that has low startup momentum and single phase motor."

Exactly. On short power outages, the coolant pressure BEFORE the expansion valve stays quite high until the valve has released quite an amount of gas into the expansion zone of the system. About one minute or so later. If you try to restart the freezer within that minute, even the public grid can't manage to start it. The internal motor current guard shuts the motor immediately out.

Are you sure, that your 3-phase heat pump has no variably controllable expansion valve? This is one of the ways to control the performance of a heat pump.

Michael

0 Likes 0 ·
marekp avatar image marekp Michael Timler commented ·

@Michael Timler

To be honest I am not sure.

I go by what the installer told me 10 years ago at the time of installation.

His argument was that it makes this heat pomp easier to repair.

I can see that when the pump needs to be restarted controller waits for 300 seconds from the shutdown before starting again.

Maybe such a timer would work for you.

P.S.

I was under impression that you have off-grid setup.

0 Likes 0 ·
Michael Timler avatar image Michael Timler marekp commented ·

Yes, I am totally off-grid, due to German regulation, where ESS needs official allowances and messing around with all kinds of authorities. But I have access to grid, so that I can test.

You see how wise your pump is constructed. It waits until restart, because the pressure has to vanish through the expansion valve before.

Michael


0 Likes 0 ·
marekp avatar image marekp Michael Timler commented ·

@Michael Timler

This is why I mentioned that delay.

Does your freezer use this method?

If not maybe external timer would help with the startup problem when supplied by inverter.

0 Likes 0 ·
Michael Timler avatar image Michael Timler marekp commented ·
Hm, if you read my explanations carefully, you will find, why this doesn't solve my problem.


Did you understand, that my freezer starts without problems right now, even with the 3ph Multiplus II off-grid? And that the whole discussion was about running only one Multiplus in a 1ph constellation during the night to save power?


I understand, when not want to study the whole thread again, but we are now at a point, where we get stuck.


0 Likes 0 ·
marekp avatar image marekp Michael Timler commented ·

@Michael Timler

You also said that this freezer would not start from 1200VA inverter.

You could use bigger Phoenix 48/3000 and it would probably manage to start your freezer, but I think that would be an overkill since by using only 1 phase at night you want to save 36W per hour of energy.

Is it worth spending Euros on the separate inverter?

0 Likes 0 ·
Michael Timler avatar image Michael Timler marekp commented ·
No, definitely not.


However, if it would have been possible to switch off two of the inverters (L2 & L3) during nighttime and have only L1 running during the night in a single phase constellation, this would have saved not only the standby consumption of a bunch of other loads of the house plus the self consumption of L1 and L2 inverters.

And this was my question (see caption), when I started this thread. Is that possible or not.

It is not, unfortunately.

Means: setting up a fourth inverter, shutting down the 3 phase system as a whole during the night and only have one inverter simply for saving 36Wh per day would have made only sense, if I could have used a cheap 100W inverter, which would be sufficient according to the nominal load of my freezer.

But the bugger starts only with an inverter bigger than 2000VA, and it is absolutely nonsense to buy one, just for that.

What I was thinking about: Shut down the 3ph-system in the night and awake it every two hours to give the freezer the chance to run for a while. On the other hand this would stress all other loads in the house, for example all loads that contain watches or time critical data stored, so that I better leave it as it is.

Michael



0 Likes 0 ·
Show more comments
sharpener avatar image
sharpener answered ·

If you keep the door shut you could probably use a timeswitch to turn off the freezer for the whole night. It will probably last eight hours or more. Maybe you would need to lower the thermostat a bit but worth doing the experiment.