simon-adam asked

Micro-invertes and multiplus

I am in the very early stages or designing an off grid Solar power for a Bush Block. I am looking to go with the Multipass 48/3000.

I will have a generator to charge the batteries and as a back up.

I am looking at the advantages and disadvantages of micro-inverters connecting the panels straight into the Multipass (looks like you do this on the outbound side) or using the more traditional MTTP (which I understand from some great videos).

Is it as simple as plugging the panel AC output into the outbound multipass?


Any thoughts or guides would be much appreciated.


Simon

offgrid
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

Yes, you can do this. Batteries will charge from the PV Inverters.
You'll need to observe the 1:1 rule, do not install more PV inverter / PV power than the power of the MultiPlus.
The MultiPlus will frequency shift to reduce or to stop the PV inverters if the batteries get full.

There is some documentation here:
https://www.victronenergy.com/live/ac_coupling:start