AC Coupling - Microgrid Total Output Capability with Foronius

I am having a brain fart with a simple question and cannot find the answer anywhere. If I have a Multi 3000Va paired with a Fronius 3000Va unit connected on AC output 1, is the total theoretical output 3000Va or 6000Va?

MultiPlus Quattro Inverter ChargerFroniusac couplingmicrogrid
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Kevin Windrem avatar image
Kevin Windrem answered ·

It's probably best to plan on 3 KVA (or 2,400 watts -- less at elevated temperatures). You'd only get contribution from the solar portion during the day, but yes the two units operating full out would be close to 6 KVA.



2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

flip-flops avatar image
flip-flops answered ·

Thanks @Kevin Windrem I appreciate you answering this